sunsen | Posted in Construction Techniques on November 24, 2008 04:00am

I’m putting in a meter base tomorrow and because of the way it’s oriented the conductors to the house, some 300 feet away, is going to require two vertical 24″ sweeps and one horizontal 36″ sweep. The conduit is 3″ and the conductor is aluminum, sized for whatever the voltage drop is over 300 feet. Is this going to be a problem when it comes to pulling the wire? Specifically, is the horizontal sweep too much? I’m not sure if that much bend is allowed anyway and will check on that.

Thanks for any input from electricians out there.

Reply

Replies

  1. sunsen | Nov 24, 2008 04:02am | #1

    I should have proofread that post. The conduit from the meter base to the point of entry at the house is about 300 feet in length with the three bends.

  2. fingers | Nov 24, 2008 08:04pm | #2

    It's hard to say without knowing how big your conductors are.  That said, it's much less pulling friction to use two gentle 45 degree sweeps than one 90 degree sweep.  Would that work for you? 

    I feel that it's slightly easier to pull thru conduit in cold weather than warm.  Even though the wire is stiffer, the friction seems to be less.

    I just did a pull yesterday in 2 1/2" conduit for a total change in direction of 180 degrees (only 60' though) and didn't even use pulling soap.



    Edited 11/24/2008 12:06 pm ET by fingers

  3. Scott | Nov 27, 2008 02:31am | #3

    When the Hydro guys pulled my service conductor through our 300' duct they poured a few cups of cable lube into the duct and used a capstan winch to pull a rope which pulled the cable. It looked like it would have been a tough job to do by hand.

    Scott.

    Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

    1. gfretwell | Nov 27, 2008 10:14am | #4

      Florida Power and Light does not seem so constrained by the NEC (they use NESC anyway) and they build the pipe with the wire in it to some extent. They don't put the sweeps on until the wire is in the horizontal run.

      1. brownbagg | Nov 27, 2008 04:21pm | #5

        my electrical buddies tell me that if you add all the degrees, they will only pull 360 degress total, if its more they have different pull ports.

        1. arcflash | Nov 30, 2008 03:37am | #10

          you are correct. A pull-station is required should you exceed 360 degrees. "Soap" is what it is called, and you want plenty of it, wire-pulling lubricant is what it is. 300 feet is a long pull, you may consider tying the rope to a truck or skid-steer or something. Use a vacuum to suck a string tied to a small bag or something to get the string through the conduit. Gradually pull in bigger string until you have a string big enough to pull the rope that will be used to pull the conductors. Tape all of your conductors the right phase on both sides, and double check it, you don't want to be wrong on that one. Not really sure what your question was, but this is pretty much how we do it.

          1. edwardh1 | Nov 30, 2008 04:11am | #11

            Some OSHA examples in the past of people getting killed pulling cables, due to the forces involved. Usuallly big cables on city streets or under city streets.

          2. arcflash | Dec 01, 2008 01:18am | #14

            OSHA has been on-site during our wire pulls before. Just be sure you can tell them where the MSDS is located.

          3. IdahoDon | Dec 01, 2008 01:48am | #15

            "...where the MSDS is located"

            *chuckle* 

            Beer was created so carpenters wouldn't rule the world.

          4. brucet9 | Dec 02, 2008 04:48am | #27

            OSHA, that's a town in Wisconsin, isn't it?BruceT

  4. JTC1 | Nov 27, 2008 05:17pm | #6

    So how did it go?

    270 degrees total bends - should have been OK.

    Jim

    Never underestimate the value of a sharp pencil or good light.
    1. sunsen | Nov 29, 2008 04:30am | #7

      I just got back from finishing up the meter base install. The PG&E inspector gave  the green light for putting in the pole and hooking up service. I found a meter base with a different knockout configuration so I'm figuring only two 90 degree sweeps. Going the 300 foot distance is next. Should be entertaining.

      1. IdahoDon | Nov 29, 2008 05:06am | #8

        No one has mentioned this yet, but pulling big wires is not always the same as smaller ones.  It's not uncommon to rig a pulley to allow additional force to help with the pull.  Use pulling soap if you haven't done it before and don't let the wire pick up dirt before it goes into the conduit.

        I'm sure there are limits to the amount of force allowed to pull a give size wire, but have no idea what those limits are.

        Often electricians make somewhat arbitrary limits on what they'll pull based on the equipment and man power at their disposal, not on a structural or mechanical limit to the pull.

        Good building! 

        Beer was created so carpenters wouldn't rule the world.

        1. sunsen | Nov 29, 2008 09:30pm | #9

          I'm attaching a pic of the situation. The 2" conduit leaving the meter base transitions to 3" as a 24" sweep just below top of concrete. The conduit will terminate at the house site just beyond the block wall in the distance, some 300' away. Hopefully the 2" section of conduit won't be a problem during the pull, (the customer side of the meterbase only had a 2" knockout as opposed to PG&E's side, which was 3"). I'll definitely be finding someone with a winch for pulling the wire. There was a fellow on this forum from norcal who owns a winch specifically for this purpose, if I can just locate his e-mail again.

          1. Scott | Nov 30, 2008 08:15pm | #12

            Wouldn't it be easier with the meter base off for the pull?Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

          2. sunsen | Dec 01, 2008 01:12am | #13

            I think PG&E will be hooking up their side of the meter base prior to my getting around to doing the trenching and pulling the wire to the house site. Otherwise, I think you're right. Seems to me it could be done with the box in place though.

          3. Scott | Dec 01, 2008 04:56am | #16

            Oh, I see. Somehow I thought the pull was on the utility side of the meter, not the house side. Now I see the issue.In my case the pull was on the utility side because we were pulling the 25KV primary to an on-site transformer in order to cut down on line loss.Are you concerned about line loss at 300'?Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

          4. sunsen | Dec 01, 2008 09:35am | #17

            Apparently the voltage drop is manageble at 300', if the conductor is sized properly. I want to do a guest house that is 1400' or so beyond the main house though. That's going to require stepping up the voltage with a transformer and stepping down again at the termination. From what I understand there is a phenomenon known as "core loss" and a few other inefficiencies that will amount to around $50/month extra on the utility bill. Not looking forward to that.

          5. gotcha | Dec 01, 2008 04:57pm | #18

            sunsen,
            http://www.power-save1200.com/1200.htmlThis device is supposed to somehow control the electricity loss in a home.Don't know if it fits your need, but seems to be well documented and the price not bad.Pete

          6. sunsen | Dec 01, 2008 06:58pm | #19

            Looks very interesting. I'm going to have to figure out exactly how this works but if it performs as advertised it would make a lot of sense to install, (for anyone, anywhere). I don't know whether the device would work on the transformers required to change the voltage for the trip up to the guest house. Technically, they're not part of the household electrical system. I sure like the idea of storing power lost to the core loss problem though. I'm going to have to look into this. Thanks.

          7. brucet9 | Dec 02, 2008 05:05am | #28

            It appears that core loss is inevitable. Certainly no outside device could affect it.http://www.tpub.com/content/doe/h1011v4/css/h1011v4_56.htmI'd guess that core loss could pretty quickly offset cost savings from using smaller wire gauge.BruceT

          8. sunsen | Dec 02, 2008 04:14pm | #29

            I guess the first thing that popped into my head reading about the power saving device was somehow being able to store the energy lost, not really stop it. That doesn't appear doable though. It would be interesting to know more about this stuff.

          9. Stuart | Dec 01, 2008 07:01pm | #20

            That Power-Save and other similar devices are basically a scam...they won't save you anything on your power bill.  Theoretically they may slightly improve the power factor if you have a lot of motorized devices running in your house, but that doesn't affect metering on a residential service anyway.

          10. sunsen | Dec 01, 2008 08:10pm | #21

            Heh, heh, I just spoke to a fellow I do a lot of work for who's an electrical engineer about the power saving device and he said exactly the same thing. Actually, he says that it's the power company who pays for lost power as a result of motors and such by way of heat in the nuetral. That's why power companies started demanding 99 percent efficiency in computers, (my friend's field). I didn't fully understand his explanation but I do know he knows what he's talking about.

          11. sunsen | Dec 01, 2008 08:13pm | #22

            Also, he said be wary of any site on the internet offering "reseller opportunities", heh, heh!

          12. gotcha | Dec 02, 2008 06:09pm | #30

            Stuart,They sure seem to document residential success.
            Of course they also are trying to get everyone into selling the product.I know or don't understand how it works, but like everyone else, am looking to save wherever possible.I try, unsuccessfully, to explain to my wife how she would quickly stop to pick up a dime on the sidewalk, but WON'T turn off anything. Like the 3 100 watt halogen bathroom light.Oh well live and learn.Pete

          13. Stuart | Dec 02, 2008 07:37pm | #31

            The Power-Save device is apparently a power factor correction capacitor (there may be other stuff inside the box, as they claim it's also a surge suppressor.)  A properly sized power factor correction capacitor will help compensate for inductive motor loads, and gets your power factor closer to 1.  However, residential utility meters don't take power factor into account, they just bill you for the amount of kilowatt-hours you've used.  So, even if this thing does what they say it does, it won't save you any money on your power bill.  Plus, if you were truely trying to correct the power factor, you'd need to switch in and out differing sizes of capacitors for each motor load as they turned on and off, where the Power-Save is just a single box with no active control.

            Here's a FAQ from the Energy Star webpage about these things:  http://energystar.custhelp.com/cgi-bin/energystar.cfg/php/enduser/std_adp.php?p_faqid=4941

            "Power Factor Correction Devices claim to reduce residential energy bills and to prolong the productive life cycles of motors and appliances by reducing the reactive power (kVAR) that is needed from the electric utility.We have not seen any data that proves these types of products for residential use accomplish what they claim. Power factor correction devices improve power quality but do not generally improve energy efficiency (meaning they won't reduce your energy bill). There are several reasons why their energy efficiency claims could be exaggerated. First, residential customers are not charged for KVA-hour usage, but by kilowatt-hour usage. This means that any savings in energy demand will not directly result in lowering a residential user's utility bill. Second, the only potential for real power savings would occur if the product were only put in the circuit while a reactive load (such as a motor) were running, and taken out of the circuit when the motor is not running. This is impractical, given that there are several motors in a typical home that can come on at any time (refrigerator, air conditioner, HVAC blower, vacuum cleaner, etc.), but the unit itself is intended for permanent, unattended connection near the house breaker panel.

            For commercial facilities, power factor correction will rarely be cost-effective based on energy savings alone. The bulk of cost savings power factor correction can offer is in the form of avoided utility charges for low power factor. Energy savings are usually below 1% and always below 3% of load, the higher percentage occurring where motors are a large fraction of the overall load of a facility. Energy savings alone do not make an installation cost effective."

          14. gotcha | Dec 09, 2008 07:12pm | #32

            Stuart,
            Thanks for info.
            I was getting serious about ordering the powersaver.They do have customer testimonials and even some exposure on TV, etc on conserving energy.Even if the advantage is mainly on electrical motors, I think the newer energy star refrigerators actually run more hours per day than older friges. One of our techs said they run about 80% of the time. Add to that furnace and AC motors and there would be more motor usage as you suggest.Getting close to retirement and we're doing all we can to lower costs.
            Am wrapping rafters in heavy foil now to combat TX heat. Even in cooler weather the heat reduction is amazing under the foil vs open rafters.Pete

          15. User avater
            Dam_inspector | Dec 09, 2008 08:27pm | #33

            That thing is basically undocumented. I watched the video, and why didn't they show the electric meter when they turned the unit off and on? My guess is that it spins faster when the Power-Save is operating. It might be a good surge suppressor, might not.

          16. Scott | Dec 01, 2008 09:00pm | #23

            Ok, glad you've got it figured. In our case (425 feet) it wouldn't work, so it cost about $7K to bring the primary and transformer onto the property. It was painful, but did it ever feel good to plug that first light in (after living with a generator for two years).Scott.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

          17. sunsen | Dec 01, 2008 10:08pm | #24

            I bet that hurt. Having the power company pull primary line for you sure can get expensive. Here in norcal it's $35/ft and that's if you do the conduit, trenching, etc. That's $35/ft just to furnish and install the conductor. Adds up pretty quick.

          18. Scott | Dec 01, 2008 10:34pm | #25

            >>>That's $35/ft just to furnish and install the conductor.Holy Smokes, that's steep. They're obviously not giving much consideration to the fact that you'll be a future customer.Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

          19. sunsen | Dec 01, 2008 11:21pm | #26

            Heh, heh, they couldn't possibly care less! PG&E does what's good for PG&E. They're pretty much the only game in town around here.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Behind the Scenes of a Concrete Batch Plant

The batch plant is your partner in getting high-quality concrete on your job site.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Podcast 551: Power Tool Batteries, Building as a Third Career, and High DIY
  • Podcast 551: Members-only Aftershow—Badly-Built Homes
  • Podcast 550: PRO TALK With Carpentry Program Instructor Sandy Thistle and Graduate David Abreu
  • Podcast 549: Energy Upgrades, Chimney Inspections, and Questions About a Home You Might Buy

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

BOOKS, DVDs, & MERCH

Shop the Store
  • Pretty Good House
    Buy Now
  • Code Check Building 4th Edition
    Buy Now
  • 2022 Fine Homebuilding Archive
    Buy Now
  • 2023 Tool Guide
    Buy Now
  • Shop the Store

Fine Homebuilding Magazine

  • Issue 314 - April/May 2023
    • 7 Options for Countertops
    • Tool Test: Wood-Boring Bits
    • Critical Details for Ductless Heat Pumps
  • Issue 313 - Feb/March 2023
    • Practical System for a Seismic Retrofit
    • Fine Homebuilding Issue #313 Online Highlights
    • Practical System for a Seismic Retrofit
  • Issue 312 - Dec 2022/Jan 2023
    • Tool Test: Cordless Tablesaws
    • Gray-Water System for a Sustainable Home
    • Insulate a Cape Roof to Avoid Ice Dams
  • Issue 311 - November 2022
    • 7 Steps to a Perfect Exterior Paint Job
    • Options for Smarter Home-Energy Tracking
    • The Fine Homebuilding Interview: James Metoyer
  • Issue 310 - October 2022
    • Choosing a Tile-Leveling System
    • Choosing Between HRVs and ERVs
    • Custom Built-in Cabinets Made Easy

Fine Homebuilding

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences

Taunton Network

  • Green Building Advisor
  • Fine Woodworking
  • Fine Gardening
  • Threads
  • About
  • Contact
  • Advertise
  • Careers
  • Copyright
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2023 The Taunton Press, Inc. All rights reserved.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Shop the Store

  • Books
  • DVDs
  • Taunton Workshops

More

  • FHB Ambassadors
  • Reader Projects
  • Podcast
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • twitter
  • facebook
  • instagram
  • pinterest

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in