I have a grounding problem with my service entrance. It is set-up like a mobile home with meter/disconnect post fed through 270′ of 4/0 pair with 2/0 return underground to the main panel in the basement. Fully inspected and done by an electrician who said all is done right: 2 ground rods 7 ft apart at the meter post with continuous 4 gauge bare ground connecting them to disconnect breaker box. The house plumbing is bonded and consequently a voltage of ~14V and 600mA can be measured between the earth and the outside faucet. Inspector and electrician say grounding is correct. My thought is in main panel separate neutral and ground bus bars and add ground rods next house and use it for all grounds (including bonding plumbing and ductwork). Any thoughts from “real” experts (excluding my inspector and electrician)?
Stephen
You said that you measured between the "earth" and "outside faucet".
What is earth? Is it your ground rods are some place else. Is the outside faucet one that is mounted on the house and connect to the house or is it an yard hydrant? And if so what is it source of water?
Is you water pipe in the house all copper?
Have you talked to the power company? Have you tried this with you your power disconnected?
Do you have an electric hot water heater?
A friend of mine ran into a similar problem with a new pool installation. The problem was with stray currents from a near by high tension line and poor grounding with the local pole.
I have a grounding problem with my service entrance. It is set-up like a mobile home with meter/disconnect post fed through 270' of 4/0 pair with 2/0 return underground to the main panel in the basement. Fully inspected and done by an electrician who said all is done right: 2 ground rods 7 ft apart at the meter post with continuous 4 gauge bare ground connecting them to disconnect breaker box. The house plumbing is bonded and consequently a voltage of ~14V and 600mA can be measured between the earth and the outside faucet. Inspector and electrician say grounding is correct. My thought is in main panel separate neutral and ground bus bars and add ground rods next house and use it for all grounds (including bonding plumbing and ductwork). Any thoughts from "real" experts (excluding my inspector and electrician)?