I drove past a home being built near where I live. probably $350k.
Two story. Will be Hardie plank siding. At the bottom of the walls, they have a bottom “band board . There is metal flashing coming down the wall behing the band board. No problem with that.
The housewrap tyvek however is terminated under (behind) the flashing. In other words if water runs down the tyvek it will go behing the flashing (that is behind the band board)
looks wrong
is it?
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
Learn more about the benefits and compliance details for the DOE's new water heater energy-efficiency standards.
Featured Video
How to Install Cable Rail Around Wood-Post CornersHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
There are no stupid questions. Here`s what I usually do. Behind the "band board" is Tyvek(although I prefer roofers felt). I bend the flashing over the top edge of band board to act as a drip cap. Aprox. 6" above the band board I slice the Tyvek in order to tuck the flashing behind it. I`m not saying its the only way to handle the situation....just the way I do.