Ewan | Posted in General Discussion on January 15, 2006 06:52am

Hello all,
Hoping for some feedback.

A buddy of mine recently bought a portable electric hot tub, and had an electrician wire it up. Tub needs a 2-pole 50A breaker, which is not available locally (or inexpensively) for his obsolete 200A BL Loadcenter breaker panel. Instead, the electrician installed a new 100A subpanel (w/o main breaker), fed directly from the terminal lugs in the main panel (I assume he swapped the single-cable lugs for two-cable lugs). I’m pretty sure the feeders from the terminal lugs are not #3 copper (or similar).
Is this approach in any way acceptable?
Would any variation on the method be acceptable?

It’s 200A service with a main disconnect switch at the meter base (on an outbuilding) and the BL panel mounted in the basement of the house.

Thanks in advance.

Ewan

Edited 1/15/2006 12:14 pm ET by Ewan

Edited 1/15/2006 4:48 pm ET by Ewan


Edited 1/15/2006 6:55 pm ET by Ewan

Reply

Replies

  1. User avater
    BillHartmann | Jan 16, 2006 07:36pm | #1

    This is outside my experience so don't take what I say as absolute.

    I think that the concept is OK, but the details are wrong.

    Some "main" panels have lugs (or holes on for lugs) on then that can be used to extend the bus to a sub-panel. However, when this is done cable and sub-panel need to be rated for the rating of the "main" panel breaker, 200 amps in this case.

    "Main" panel - while there is a service entrance in another building this panel might be treated as a sub-panel (neutral isolated from the ground bus/ground electrode system) or it bonded and treated as a main panel. However, in either case a disconnect is needed at the house. A main service disconnect can have upto 6 different "switches". Don't know if the same is allowed for the disconnect at an "outbuilding" or if you are only allowed one disconnect (per service).

    Now there are cases where you can have multiple taps off at the service entrance. Commonly done with you have a 320 or 400 amp service and multiple "main" panels. Each panel will have a set of wires, rated for the panel size, back to the meter.

    Possibly that could be done here, but in that case the new panel would need a 100 amp main breaker and 100 amp wires back to the 200 amp disconnect. (Main breaker might not be needed if the new panel is filled and the total is no more than 100 amps and you can get by with the 6 or less disconnect rules).

    However, the feeder to the house is protected by the 200 disconnect at the meter so I don't know if there is really a safety problem or not.

    Sum, it does not sound right. However, I really don't have enough background to prove it one way or another.

    1. Ewan | Jan 16, 2006 08:51pm | #2

      Many thanks for the reply Bill.

      I'm not an electrician, but the set-up doesn't seem right to me... and it's certainly not the 'conventional' method for hooking-up a sub-panel where the sub is protected by a breaker in the main panel, with appropriately sized feeders.

      Regards,Ewan

  2. User avater
    maddog3 | Jan 17, 2006 09:31pm | #3

    Hi Ewan,
    I don't know what the CEC requires as far as a main breaker in the sub -panel...

    ..It would be something I would put in though

    .. and I will say that since the main disconnect is 200A then the wire to the new sub will have to be at least 3/0 Cu. it can then be fused at 100A with a breaker backfeeding the sub-panel......which might be difficult fitting the 3/0 under 100A lugs

    1. User avater
      Nuke | Jan 17, 2006 10:03pm | #4

      I didn't know you could wire a subpanel off the main panel via the main luhs. I always was recommended to wire it via a breaker of considerable means. How does one know whether or not their main panel's lugs can be used in this manner?

      1. User avater
        maddog3 | Jan 18, 2006 02:13am | #9

        one hole....one wire... most inspectors here won't allow taps to be smaller than 4/0
        100A or smaller comes off a breaker ...

        1. User avater
          Nuke | Jan 18, 2006 05:30pm | #11

          Thanks for the enlightenment. I'm going to be putting in a 100A sub-panel and had planned for a breaker-method.

    2. brownbagg | Jan 17, 2006 11:46pm | #5

      main disconnect is 200A then the wire to the new sub will have to be at least 3/0 Cu.no. the subpanel is wired with what ever the sub is. If its a 100 amp sub then its wire with 100 amp wire( dont have my book here) If its a 60 amp sub then wire with 60 amp wire.. 2+3=7

      1. User avater
        maddog3 | Jan 18, 2006 12:45am | #6

        I thought the #3was bolted onto the bus,....what am I missing,if the guy used #3 then that is too small...it don't matter what the sub is that its feeding...the new sub is fused at what ever the main disconnnect is...unless I read the post wrong

        1. User avater
          BillHartmann | Jan 18, 2006 12:48am | #7

          I gathered that it was bolted to the incoming feeder to the breaker in the "main" panel.

          1. Ewan | Jan 18, 2006 01:05am | #8

            Thanks to all for the replies.The feeds to the new subpanel are tapped off the incoming feeder to the 'main' panel (i.e. the only over-current protection for the subpanel are the main disconnect fuses).I'm pretty sure the feeds to the subpanel are #6 CU, which I gather is 'okay' for the lone 50A breaker that's currently installed, but no good to accommodate possible future branch circuits.I'm not an electrician, but I'm wondering if this isn't a kludged application of the "10 ft tap rule"?http://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/FeederSecondaryTapRules~20020326.htmI forgot to mention that the new subpanel is immediately adjacent to the main panel.... apologies.

            Ewan

            P.S.  Maddog, yep they're ~supposed~ to be licensed up here... just not sure this one was.

             

             

            Edited 1/17/2006 5:15 pm ET by Ewan

            Edited 1/17/2006 5:17 pm ET by Ewan

          2. cap | Jan 19, 2006 02:30am | #12

            Ewan,

            I'd say that the installation is not Code-compliant.  Although the new subpanel now has only a 50 amp breaker in it, it'd be very easy to increase the load on the tap by installing new breakers.  For the tap rule to be apropriately applied, I think the tap conductors would have to be rated at the subpanel rating--100 amps.

            Even then, I think it's not a good design to apply the tap rule to a subpanel that's not protected by a main breaker.  I believe that the tap rule was intended to apply to situations like a cooktop being tapped off of the oven conductors w/o needing overcurrent protection, or other situations where there's a set load supplied by the tap.

            As far as sizing the feeder conductors--you're right, even if they were protected at the main panel with an appropriately-sized breaker, using AWG 6 is pretty short-sighted; no room for expansion.

            And as to the post about conductor size being determined by subpanel ampacity rating, that's only part of the story.  The feeder conductor size is determined by the subpanel ampacity and any votage drop adjustments, temperature corrections, and conduit fill adjustments.  The feeder (source) breaker must be sized according to the subpanel ampacity.  A 60 amp subpanel must be protected by a 60 amp (or less) breaker at the supply panel, and has to be fed with AWG 6 copper  if THHN or equivalent 90C insulation.  [edit by CAP: to clarify, actually, the sub only has to be supplied by AWG 6 copper if it's being fed by a 60 amp breaker on the supply panel.  It's perfectly Code-compliant to feed a 60 amp-rated subpanel using a 20 amp breaker, if your calculated load on the subpanel is 20 amps or less.  In this situation,  the feeder conductors could be AWG 12 copper.  I'm not saying it's a good idea, but it'd be Code-compliant.  The point is, the feeder conductors have to be sized to supply the load, taking onto account corrections and adjustments to conductor ampacity, and the feeder breaker has to be sized based on the feeder conductor size.)

            But, if it's a 200 foot run to the subpanel (and you want to keep voltage drop to the recommended 5%), and it's in an attic that's going to get to 150F, and there are more than three current-carrying conductors in the raceway, then those conductors will have to be much bigger than AWG 6 copper.

            Cliff

            Edited 1/19/2006 1:08 pm ET by CAP

          3. Ewan | Jan 19, 2006 03:16am | #13

            Terrific Cliff... many thanks for the post.
            Based on my electrical-wiring self-education, I didn't ~think~ the install was code-compliant (be it NEC or CEC)... I've suggested my buddy find himself a 2-pole BL breaker (refurbished ones available online) and feed the subpanel properly. Regards,
            Ewan

        2. User avater
          maddog3 | Jan 18, 2006 02:17am | #10

          that don't happen here too much.........and this is a good example why

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

A Classic Paint Sprayer Gets a Thoughtful Refresh

The Titan Impact X 440 offers great coverage with minimal overspray.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Fine Homebuilding's Author Guidelines
  • Podcast Episode 693: Old-House Hazards, Building Larsen Trusses, AI in Construction
  • FHB Podcast Segment: Finding Hazardous Materials in a Fixer-Upper
  • A Classic Paint Sprayer Gets a Thoughtful Refresh

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in