moltenmetal | Posted in Construction Techniques on November 8, 2004 05:41am

We’re planning a 2-storey addition along the entire 38′ length of the west wall of an existing 1.5 storey house.  The existing house has a poured concrete basement, and the first floor is supported by 2×8 full dimension joists with a central beam.  The addition’s joist span will be 12’4″, and though the code would permit me to go with 2x8s on 12″ centres, I’d like the floor a little stiffer than the code minimum (because the floor finish will probably be ceramic tile).  So I’m going with 2x10s on 16″ centres.

To complicate matters, the existing house is brick veneer, and the first course of brick starts at the TOP of the sill plate.  So even if I went with 2x8s, I’d have the same trouble finding/making a place for my new joists to bear on.

I’m considering two options to support the addition’s joists on the existing wall once the brick is removed:

Option 1:  remove brick veneer, saw the concrete wall to the required level and set a new 2×4 sill plate to support the new 2x10s.  Bolt the sill to the existing wall using sleeve/wedge anchors.  Install a conventional header (rim?) joist on top of the sill and install joists as normal.

Option 2:  remove brick veneer, notch joist ends to bear on existing concrete, install a 2×4 or 2×6 ledger board by bolting with wedge/sleeve anchors to the existing concrete, so the un-notched portion of the joists have something to bear on, then install continuous blocking between the joists to take the place of the missing header/rim joist

I’ve attached sketches of both methods if my description isn’t clear.

Option 1 is 2×38′ of concrete sawing, plus it weakens the existing wall under the existing joists- not something I fancy.  Option 2 is far less work, leaves the existing wall intact, and should transfer the loads from the floor into the foundation wall just fine- plus the ledger isn’t really bearing 100% of the load, it’s merely keeping the joists from splitting at their notches. 

Any other options?  Any reason you see that a building inspector/plan reviewer dude would not like option 2?

Thanks in advance for your advice! 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. blue_eyed_devil | Nov 08, 2004 06:23am | #1

    I would install a doubled 2x8 ripped to size above the existing brick foundation, holding it flush with the foundation. I'd then hang all the new 2x10's off of it using joist hangers.  This is a very common situation (bottoms of joist not aligned).

    blue

    Warning! Be cautious when taking any advice from me. Although I have a lifetime of framing experience, some of it is viewed as boogerin and not consistent with views of those who prefer to overbuild everything...including their own egos

    Additionally, don't take any political advice from me. I'm just a parrot for the Republican talking points. I get all my news from Rush Limbaugh and Fox and Friends (they are funny...try them out)!

  2. User avater
    Dinosaur | Nov 08, 2004 06:26am | #2

    First of all, I really don't see the advantage to you of going for 2x10 on 16's instead of 2x8 on 12's--you'll have at least as stiff if not a stiffer floor with that many more joists. You're adding 25% more wood by going to 12" centers while bumping the joists up 2" only give you 20% more wood under your floor. Yes, I know that 20% is in depth section, but the old rule of thumb still ought to work in your favour. If you're still worried about cracking any ceramic finish floors, you can install them over Ditra.

    Second, why don't you simply remove the veneer and bolt on a 4x4 ledger with sleeve anchors, then support that ledger with a stud wall down to the footing on the outside of the foundation wall. This way you can just hang the whole addition on that ledger and not have to worry about notching or concrete sawing or whatever, just a bit of digging which you'll have to do anyway (I'm assuming here you're also expanding the basement under the new addition).

    Dinosaur

    'Y-a-tu de la justice dans ce maudit monde?

    1. moltenmetal | Nov 08, 2004 07:07am | #3

      Blue:

      Nice solution! Only one question:  can you fit all the hanger fasteners for a 2x10 hanger on a 2x8?  If I remember correctly, the fastener holes stop a fair ways above the bottom of the hanger, but exactly how far I'd have to check.  I won't have to rip much off the 2x8s- by my measurements, the brick ledge is exactly the same thickness as the existing wall's sill plate, which is full dimension 2", so I'd end up ripping ~1/2" off the new 2x8s to make the new header.

      Dino:

      Whether I go with 2x8s on 12" centres or 2x10s on 16" centres, I'd still need a means to tie the new header joist to the concrete wall- or would I?  Would bolting the new 2x8 header joist through the existing 2x8 header joist (with spacers if necessary) be sufficient so that I wouldn't need to bolt on a ledger?  If so, then I'm going with 2x8s for sure!

      Here's why I figured I'd be better with the 2x10s:  I'm planning to staple up PEX under the subfloor and I would like two tube runs per bay.  Two tube runs per 12" bay would be overkill, and one wouldn't quite be enough.  And the span tables tell me I can do up to 13'6" with 2x10 x 16" oc whereas I'd only be just barely good enough at 12'6" max span for 2x8 x 12" oc.  With the 2x10s, the extra wood's in the depth direction which should give me a stiffer floor.  Plus the 16" centres will give me more room to run plumbing etc. too.  It just seemed like a better way to use the extra wood.

      You're right- I am putting a basement under the addition, and have to underpin that long wall.  A sub will dig the main hole but the u/pin slogging will be done by hand, so I will be doing some digging- so much that I'll be totally sick of it before I'm done.  If nothing else, that wall under the ledger would be useful as a place to chase wires...So:  I have to run this wall down to the footing:  how do I do the floor slab?  The new wall must land on the footing, not the slab, correct?

      1. User avater
        Dinosaur | Nov 08, 2004 07:49am | #4

        I'm not following you about that 'header joist'--not a term used around here. Do you mean the rim joist? If so, it's kind of optional in this scenario as long as you've got solid blocking (full 2x8 blocks) between the joists at the ends and cross bracing every 5-6 feet. You'd want a rim joist at the outboard end; but it's not really necessary up against the concrete foundation wall. In any event, I don't see the utility in connecting it through to the existing floor in the old section. Any nailed connection would be in tension and worthless; you'll get more holding power from nailing the joist bottoms to the ledger.

        Installing that ledger is no big deal. Buy yourself a Bulldog and have at it; you'll be done before you know it. Theoretically, you could build a stud wall up against the outside of the foundation wall and skip the ledger and nail the joists to the top plate of that wall. But lag-bolting a ledger to the concrete wall will give you a more solid connection laterally for the entire new section as you'll be nailing in shear into something that is held onto the face of the foundation wall very well.

        I consider that supporting wall essential to this set up, as you will be dropping a two-storey structure on top of that ledger. Not the kind of load you want to hang on just a few bolts, no matter how beefy....

        As far as the supporting stud wall going down to the footings or the floor slab, I should have said floor slab. I was thinking both ahead of and behind my assumptions simultaneously when I wrote that....

        You definitely don't want to pour a slab on top of the foot of a stud wall already in place...although I've seen it done (couldn't believe it when I did see it; the so-called builder's justification was that he didn't want to pour the slab until he had a floor over it to protect it from possible rain. Aside from the fact that floors don't keep rain out, I had to wonder whether he'd ever heard of a tarp...).

        Finally, on the 12" vs 16" joist bays and the PEX--I assume you're doing that for under-floor heating. So in a 16" bay you've got 14½" of clear space; you wanted to put in two tubes; that makes it 7¼" say 7" OC for the tubes. Why don't you just lay out the same 7" OC spacing working around your 12" joist bays? Some bays you'll have one tube, some you'll have two. But upstairs on the floor you'll have more even heat distribution.....Dinosaur

        'Y-a-tu de la justice dans ce maudit monde?

        1. moltenmetal | Nov 09, 2004 04:40am | #6

          Dinosaur:

          Your explanation is very clear.  Yup- delete the word "header joist" everywhere I said it and replace it with "rim joist"- that's what I meant.  Funny that when I looked it up, neither my copy of Carpentry and Building Construction, nor the Ontario Building Code, refer to what we're talking about as a rim joist, so I got confused.

          Fortunately, there's an advantage to underpnning in my case:  Once I'm done, I'll have the top of the existing footer, well above the new floor slab, as a good landing place for the supporting wall.  Good thing too- dunno if the building department guys would like me landing that supporting wall on top of the floor slab, since it'll have foam insulation under it in this case (PEX in the slab too...)

          We agree that the supporting wall is essential in your design- I wouldn't hang my two new storeys entirely off bolts in that old concrete either.  In my idea, I notched the joists so that they'd be resting on top of the concrete, and the ledger would just resist their desire to split where they're notched.  But before your post I was wondering if I could get rid of your bolted ledger by bolting a new rim joist through the existing rim joist, which is of course nailed in shear to the existing sill plate which is bolted to the top of the foundation wall.  You're right that my nailed joints would be in tension and hence useless unless I also used hangers...which pretty much puts me back to Blue's method.  But I like your supporting wall since I'll need one to chase wiring through anyway.

          Bulldog?  Tell me more!  I'm looking for a good, heavy-duty hammer drill to replace the POS Makita piece of crap I bought at Canadian Tire in a fit of cheapness. 

          1. blue_eyed_devil | Nov 09, 2004 05:19am | #7

            piece of crap I bought at Canadian Tire in a fit of cheapness. 

            We never learn...do we?

            blueWarning! Be cautious when taking any advice from me. Although I have a lifetime of framing experience, some of it is viewed as boogerin and not consistent with views of those who prefer to overbuild everything...including their own egos

            Additionally, don't take any political advice from me. I'm just a parrot for the Republican talking points. I get all my news from Rush Limbaugh and Fox and Friends (they are funny...try them out)!

          2. User avater
            Dinosaur | Nov 09, 2004 07:49am | #8

            Bosch Bulldog. It's an SDS-Plus rotary hammer that will put holes up to 1.25" in concrete, 1.0" in hard stone IIRC. If you needed anything with more bang than that (which you don't, for this job), you'd be talkin' Kango, and that's rental-type gear unless all you do all day everyday is bust up concrete.

            The Bulldog makes holes for 3/16" Tapcons in less than 2 seconds (literally) and will sink holes for those Hilti-type anchors in a minute or two each. Figure 38 feet of ledger w/bolts 24" OC you got 20 bolt holes to drill, you oughta be done in an hour including layout, concrete drilling, drilling the 4x4 and bolting it up. Piece of cake....Dinosaur

            'Y-a-tu de la justice dans ce maudit monde?

          3. moltenmetal | Nov 10, 2004 02:00am | #9

            Dino:  sweeet- gotta look up that Bulldog.  Already got a good, powerful non-hammer corded 1/2" drill, so a rotary hammer might be a better choice.

            And Blue- you're right, we never learn.  Cheap tools are fine for occasional use, but a hammer drill?  What was I thinking?!  I was suckered by the brand name and the price- I have lots of (earlier generation) Makita stuff that I love and wouldn't be parted from, but this $99 (CDN) hammer drill is a total POS and I should have known better.  You can smell the insulation and the case starting to melt any time you try to get it to deliver any torque...I figure it's good for about 10% duty cycle- any more than that and it'll be toast.  It's the only drill I'll loan out, because I'm kinda hoping somebody'll actually fry it for me...

          4. blue_eyed_devil | Nov 10, 2004 03:44am | #10

            You shoulda bought it from a big box...then you can take it back!

            I used to buy all the best tools. Now, I'm not so in love with tools and occasionally will take a stab at something cheap. I'm usually disapointed and am glad when I can take it back. Often though, I just give the stuff away to whoever I'm complaining to at the moment. Everyone is happy to get something for free...even if it is crapola.

            But the best is when that cheapie works better!

            blueWarning! Be cautious when taking any advice from me. Although I have a lifetime of framing experience, some of it is viewed as boogerin and not consistent with views of those who prefer to overbuild everything...including their own egos

            Additionally, don't take any political advice from me. I'm just a parrot for the Republican talking points. I get all my news from Rush Limbaugh and Fox and Friends (they are funny...try them out)!

      2. blue_eyed_devil | Nov 08, 2004 04:42pm | #5

        Your concern about which hanger to use is well founded Molten. There is a huge selection of hangers that will specifically cater to your needs. I'd peruse the simpson.com site and maybe send an email request to them an ask for their recomendations.

        I'd probably just use hangers suitable for 2x12's depending on how picky the inspectors are. If they're real picky about stuff like that, I'd run the setup by them before I did it.

        blueWarning! Be cautious when taking any advice from me. Although I have a lifetime of framing experience, some of it is viewed as boogerin and not consistent with views of those who prefer to overbuild everything...including their own egos

        Additionally, don't take any political advice from me. I'm just a parrot for the Republican talking points. I get all my news from Rush Limbaugh and Fox and Friends (they are funny...try them out)!

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Mortar for Old Masonry

Old masonry may look tough, but the wrong mortar can destroy it—here's how to choose the right mix for lasting repairs.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Fire-Resistant Landscaping and Home Design Details
  • A New Approach to Foundations
  • A Closer Look at Smart Water-Leak Detection Systems
  • Guest Suite With a Garden House

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data