Utility pipe material selection:

Wayfarer | Posted in Construction Techniques on April 6, 2004 02:26am

Well, I’m not down to the wire, but switching gears outside again; have a trench open to lay in sewer and then 12″ above and to the side, three utilities: gas, water, and electrical.

I’ll use 1 1/2″ iron for the gas line, plastic conduit for the electrical, but what about the water?  I have the option to use either copper or PVC.  None of the latter (copper and iron) need to be wrapped.  I’m thinking maybe going with a schedule 80 for the water line.  Any thoughts?

All these utilities (except the sewer which is the new line for the new house) will be servicing a cottage on the existing lot; the utilities are coming from the new-construction house.

Also, as a side-note; any thoughts on using ABS vs SDR 35 for the 4″ sewer lateral?

Thanks ahead of time for any suggestions.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. brownbagg | Apr 06, 2004 03:12am | #1

    everybody here just use schedule 40 white pvc for supply

    1. User avater
      Sphere | Apr 06, 2004 03:35am | #2

      my town water and spring both are 1'' black abs with no problems..Kentucky here.

      View Image

      Spheramid Enterprises Architectural Woodworks

      Repairs, Remodeling, Restorations. 

      1. User avater
        BillHartmann | Apr 06, 2004 04:02am | #5

        ABS or polyethelne?

        I have never hear 1" abs, not to say that it does not exists.

        1. User avater
          Sphere | Apr 06, 2004 04:12am | #6

          maybe a confusion on my end..I always THOUGHT it was ABS..black coils..grey fittings,, hose clamps and compression fittings..some one musta called it that in my childhood an it stuck..never liked it all that much, but now a convert..being as they came out to dig up my main, and fixed it in 10 mins. flat with two compression unions and 1 foot of new pipe.

          Slap me if I'm wrong..woodworking..stick to woodworking Duane.

          View Image

          Spheramid Enterprises Architectural Woodworks

          Repairs, Remodeling, Restorations. 

          1. WayneL5 | Apr 06, 2004 04:37am | #7

            Oh, yea, speaking of fittings, I would not use the gray plastic fitting with the polyethylene pipe.  I only use brass or stainless steel hose nipples, with stainless steel clamps.  Stainless if I'm connecting to steel pipe, brass if connecting to copper.  If the clamps are to be burried, I don't use the ones with a stainless band but a steel screw.  I use all stainless clamps for burial.

          2. User avater
            Sphere | Apr 06, 2004 04:57am | #10

            makes sense to me..all of my unions are compression (brass) and tie right to my newly run inside copper..

            I musta been wrong about the ABS/polyethlyne names..

            I just hate plumbing..always is ONE MORE trip to the store for ONE MORE fitting..I don't do that much, but have learned to grab contactor packs of fittings..even if I just need 2..<G>

            View Image

            Spheramid Enterprises Architectural Woodworks

            Repairs, Remodeling, Restorations. 

  2. User avater
    SteveInCleveland | Apr 06, 2004 03:51am | #3

    What, does everyone have something against me?  What did I ever do to you?

    signed,     

                galvanized pipe

  3. WayneL5 | Apr 06, 2004 03:59am | #4

    Copper will hold up well, but burried too close to iron might accelerate the decay of the iron.  If you go with PVC, the extra money for schedule 80 is probably worth it because it will be resist physical damage more.  Schedule 40 would be pleanty adequate for the water pressure.

    I'd use black polyethylene, though.  The big advantages are flexibility and being seamless end to end.  In my opinion its the most reliable of all the options.  Especially in earthquake country.

  4. DavidThomas | Apr 06, 2004 04:39am | #8

    Schedule 80 PVC for the water, if allowed.  One advantage of PVC over copper is that it is so cheap, you can afford to go up a size and be sure you have no pressure drop on the service line.  I'm not allowed to, here, because you have to be able to thaw your lines.  When you step up to speciality plastic pipe with heat trace embedded in it, you might as well go with copper.

    I'd strongly recommend polyethylene gas piping.  Has to be made up at the plumbing supply, but give them dimensions and they'll fit the metal 90 degree sweeps to each end.  Bury that with a tracer wire and you've got no joints below grade.  And you're not trying to crank on black iron pipe and fittings in a trench, with dirt falling, etc.  Of course, check that it is approved for use locally.  Check with both building department and gas company, sometimes the gas company is stricter than local code.  But I love the stuff.

    But 1-1/2" on the gas?  Is the regulator not at the house?  I'm used to seeing (CA, WA, AK) gas coming to the house in medium (5 psi) or high (60 psi) and then regulated to 1/4 psi = 7" w.c.) at the house.  So you only need 3/4 or 1" for the service line. 

    Ah, just re-read your post.  So you are coming off AFTER your regulator/gas meter hence the need for the huge gas line.  If the cabin is always part of the property, that's probably the way to go - you save the meter fees on the second meter.  I plumbed my own cabin for its own services so it could be sub-divided at a later date.

    Sphere: Slap!  The coiled black stuff is poly, not ABS.

    David Thomas   Overlooking Cook Inlet in Kenai, Alaska
  5. davidmeiland | Apr 06, 2004 04:40am | #9

    1-1/2" gas is huge. Got a kiln or something in there?

    I think it's worth asking the inspector what he wants you to use. Last jurisdiction I worked in only wanted copper water service, no plastic. Here they'll accept PVC but prefer copper, and no buried black iron for gas, only poly. Or, talk to a plumber and ask what's typical in your area.

  6. remodelerdw | Apr 06, 2004 07:03am | #11

    My primary trade is underground utility / sitework contractor.  I remodel on the side.

    >1 1/2" iron for the gas line

    Wow.  Utility company uses SDR7 IPS polyethylene here, yellow plastic.  1 1/2" is commercial service.

    >plastic conduit for the electrical

    NEMA conduit (grey) is standard for electrical here, but sched-40 is okay.  The grey conduit is cheaper & thinner walled, and works well.

    >what about the water?  I have the option to use either copper or PVC.

    Water service here is either copper in 60' or 100' rolls 3/4" or 1", or SDR9 polyethylene blue plastic.  SDR7 black plastic (thinner walled) is sometimes used for irrigation / well services.  The blue poly is a first choice - cheap, 100', 300', or 500' rolls in 3/4" and 1" and you won't have any problems.  Try to avoid coupling and if you do use standard compression fittings - AY McDonald, Ford, or Muellers are the only ones you should use for buried service.  But don't use them, buy a bigger coil. 

    >any thoughts on using ABS vs SDR 35 for the 4" sewer lateral

    Don't use ABS.  It's not approved in anyone's code that I'm aware of.   Use SDR35 unless your depth of bury is greater than 12', then use SDR26.  I would run a 6" lateral, 4" tends to clog.  Pay the extra bucks for gasketed fittings and pipe, the solvent-weld stuff is junk and will cause you grief.

    An underground utility supply yard, such as Hughes, Ferguson, U.S. Filter, etc. will have your best price.  Present yourself as a knowledgeable contractor at the cash desk.  Also, I assume you're not running the lat in the same trench as your water service.  Bad idea if you are.  Ten states code require 10' horizatontal on parallel runs and 18" vertical separation on a crossing of water and sanitary, and that is the uniform code for most of the country.

    remodeler

    1. User avater
      Wayfarer | Apr 06, 2004 07:58am | #12

      Yikes, I don't think I've ever had this many responses this early in a post I've made.  Thanks heaps for the suggestions and help.

      Some of you guys are giving me a little bit more benefit of the doubt as far as what I am familar with; I am not a plumber by trade, and of all the sub's that I worked, and continue to work with, the plumber(s), for whatever reason, at least on my project were the toughest to deal with--in fact, I was sued by one of the first plumbers that was on my site--that's a whole other story, which I posted about almost a year ago...I'm trying to put that whole thing behind me.  Ironic, cuz I had a few issues, which I thought there would or would expect to be with the group that did my foundation and framing, but the latter, save the dickhead principal of the company, are back on my project doing some additional work.  I've also had a number of their other carpenters on my job doing side work for me; but all the latter is a sidenote.

      Wayne, it never even crossed my mind about the interaction between copper and iron, or the potential for it, in a trench...yeah, yeah, I know about that when joining the latter two materials for say water, but didn't think about in a trench; another reason to consider pvc for water line; or at least put the electrical conduit between water and gas.

      David, it never even crossed my mind going up in diameter size for the water which is an excellent point.   I use to work for an ol' division of Johns Manville bought by a Taiwanese conglomerate (funny, this was the 80's when foreign companies were buying American companies and employing Americans...guess that's a whole other post and thread) so kinda know hydraulics or the dynamics the of; wouldn't head-loss fall into some consideration?  I mean usually in gravity flow you go up in diameter, but I'm not so sure about in water supply and pressure; it seems like gas (I wrote 1 1/2", but to be sure, it might be 1 1/4"...I need to check what is poking out my structure where the original design is reflected) falls in between this water and gravity issue--but then gas is operating at such a low pressure, that distances to use i.e. the cottage in this case is made up by size of the pipe, volume.  Anyway, I'm intrigued by this idea about sizing up as on this line as I have a pool and landscaping to a large extent to contend with down the road.

      davidmeiland and remodelerdw--you guys keep refering to plastic pipe/poly-whatever gas lines; I'm interested in that, but get this; I email with the head building inspector with my City and he said if I used ductile iron for the sewer, I wouldn't need to use any sand in the trench for backfill!  I was like, "People still use iron for sewer laterals!!!"  I don't know, I'm in the Bay Area and it is still a Union area in some of the trades.  So I don't even want to think what is going on with poly-pipe for gas...maybe I should ask.

      Further remodelerdw--good comments about the sewer lateral and sizing up and using gasketed fittings (did I comment that I use to work for Johns Manville?), I didn't really consider that; in my area, this could/would suit well in earthquake country--however, I am on bedrock where this is not always an issue like being in the Marina District in SF proper.  I like the idea about possibly upsizing with the lateral.  It will be almost 100' to tie into the six inch City main that was installed some almost 70 years ago.  The only thing is I have plenty of drop; probably on my stretch (without looking at my topo) about 12 feet (and yeah, I just had to look at my topo).

      Thanks again...

      1. davidmeiland | Apr 06, 2004 08:26am | #13

        Where are you specifically in the Bay Area? I know lotsa folks there and probably someone you could call for info if you like. Seriously, find out what the city and PG&E are going to be OK with for the various lines.

        1. User avater
          Wayfarer | Apr 06, 2004 08:41am | #14

          david, I am in San Mateo County: just had PG & E out on site last week to inspect my trenching for the service line (nothing that I have been outlining above) and my project or trenching "failed."  Nothing that I had done; what I had done was fine with the inspector.  But the location of the meter was different on his paperwork and mine...so he was going to get jiggy with the designer and hopefully get my project pushed through and schedule this week.  This is the same organization that failed to mark out in my trench the live underground electrical wire that services the house across the street (pretty much everyone else is overhead, including my new construction)...what worries me is that I had a laborer on site to dig my trench and he could conceivably been injured by this mishap.  If PG & E gives me any $hit on this inspection or service hook-up, I am going to read them the riot act...it is unconsciousable (sp?) that they would miss this and not mark adequately on the City's easement that there was live wire underground; the gas line they did mark which is why I was digging...

      2. DavidThomas | Apr 06, 2004 09:04am | #15

        > > "but I'm not so sure about in water supply and pressure

        > > I'm in the Bay Area and it is still a Union area in some of the trades."

        For the potable water service line, 3/4 is minimum for flow but not ideal. For up to 100', I'd go 1" minimum. I've got 400' myself but had to use copper because at only 11' deep it is too likely to freeze and need thawing. So I went with 1-1/4 copper. PVC and I would have used 1-1/2 or 2 - better for fire protection. (And I have no meter which sets an upper limit on flow in many installations.)

        I was trying put ABS in Oakland in the late 80's and when asked why ABS wasn't allowed, was told, "Cast iron worked fine in 1920, works fine now." I took it as extreme plumber conservatism but it could have been a full-employment issue for his brother-in-law. At least they allowed no-hub instead of akem and lead!

        David Thomas   Overlooking Cook Inlet in Kenai, Alaska

      3. User avater
        BossHog | Apr 06, 2004 10:17pm | #18

        I'm under the impression that you can't run water and sewer lines parallel with each other unless they're 10' apart. (At least here in Illinois)

        Or am I all wet ???Enter action with boldness . . . Any mistakes you commit through audacity are easily corrected with more audacity. [ Robert Greene and Joost Elffers, "The 48 Laws of Power,"]

      4. Remodeler | Apr 07, 2004 01:20am | #19

        Wiley,

        I've seen ductile used for sewer main / lats, primarily when it's very deep and we're compacting backfill in lifts and don't want to burst the pipe (such as in front of houses where the driveways would settle with uncompacted fill).  But it's expensive, probably $6/ft for 6" and the 4" is hard to come by out my way.  It's not commonly used so small.  Sand is expensive too though.

        Your drop gives you a 12% fall, and at that rate your effluent will outrun your solids and you will have tremendous problems with sewer clogs.  1-2% is doable.  It sounds like you need a small manhole to take that much drop.

        Good luck,

        remodeler  (dw is my wife's account)

        1. User avater
          Wayfarer | Apr 07, 2004 06:23am | #21

          I see a bit of your point, and now I'm like the ol' (or young at the time) sales rep in the PVC industry; the PVC will be non-porous, unlike clay (yeah, it ain't glazed in the inside), and ductile iron (that ain't smooth or slick on the inside), so yeah, the solid may have to play catch up, but it will be with the next flush or whatever, the solid will always be behind to the prior flush.  Plus, given that there will be far more effluent than solids, I really don't see the biggie.  The only reason why engineering gets into this whole drop, 1/4" to a foot or whatever, is because there isn't the grade like you can realize in my situation--at least that's my rational in my situation and with what little experience I've had in the industry as a whole.

          Further:

          I've seen ductile used for sewer main / lats, primarily when it's very deep and we're compacting backfill in lifts and don't want to burst the pipe (such as in front of houses where the driveways would settle with uncompacted fill).  But it's expensive, probably $6/ft for 6" and the 4" is hard to come by out my way.  It's not commonly used so small.  Sand is expensive too though.

          Actually, from my experience in the industry, one could install a large diameter paper roll and if installed properly, would last it's design length to any other material.  I have to agree that more rigid/solid materials make up for poor installation.  But if installed correctly, PVC is better in the long run which I can clearly outline.

          However, the earlier point is taken where I will at least install some additional cleanouts in my system more than likely.

          JoeH, thanks for that; I really need to research, and am a bit in the dark about options (if I have them in my City) for the gas.

          Boss, I forgot to add yesterday; yeah, in our City spec the sewer and water can share the same trench, but must have a degree of separation (water 12" up and 12" to one side of the sewer line) as long as the materials in the trench are approved for use in the house.  They are adopting or use 2001 UPC 718.3.  Which at second glance, with the materials I am using, I'm not even sure if I need the separation outlined above.

          Edited 4/6/2004 11:25 pm ET by Wiley

          Edited 4/7/2004 11:44 am ET by Wiley

    2. User avater
      BillHartmann | Apr 06, 2004 04:29pm | #16

      "NEMA conduit (grey) is standard for electrical here, but sched-40 is okay. The grey conduit is cheaper & thinner walled, and works well."

      'Standard' PVC electrical conduit is sch 40.

      But there is also a sch 80 that is used where there is chance of phyiscal damage.

      1. User avater
        Wayfarer | Apr 06, 2004 06:14pm | #17

        Thanks for the additional comments.  When I am mentioning ABS I am thinking the stuff used inside the house where I would solvent weld the joints with a coupling in the trench.  My impression from working/selling "plastic" pipe (I only dealt with PVC pipe) in the 80's was that ABS is less impact resistant to PVC i.e. SDR 35 in this case.  Once either are in the trench, I don't know that there is heaps of difference.

        Bill, you remind me of a story of a new electrical panel I put in, in a house I owned in the early nineties; I remember running conduit from the meter to the roof.  I remember researching or working with the issue of schedule 80 vs schedule 40.  Having to use schedule 80 up till a certain height where there might have been some impact threat; I don't know, maybe someone wielding a hammer close to the conduit or something like that.

  7. joeh | Apr 07, 2004 01:36am | #20

    That 1 1/2" iron pipe sounds like "we always did it that way."

    Try the yellow plastic coated stainless stuff, no joints and cheaper.

    Although you may be in the land of Union job guarantees and it won't be allowed.

    Gotta keep them good Union Workers working, even if it costs twice as much.

    Joe H

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding the Right Fixer-Upper

Get expert guidance on finding a fixer-upper that's worth the effort.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data