PEX Safety?

dogfish | Posted in General Discussion on April 2, 2008 03:11am

I have a customer who is an engineer and has researched just about everything going into his new house.  He has raised concerns about both the safety of PEX from a chemical standpoint and also potential problems with water pressure.  See the links he sent me below.  I’m a GC and lean on my plumber to make sure the water lines are the right size and all but I’ve never seen him do any calculations or anything.  The last 4 houses I built(and several I worked on before that) all had PEX and I’ve never had any complaints from my customers.  In this area at least it seems like it’s all anybody uses unless copper is specified in a really expensive house or something.  Is there another water line alternative other than copper?  I guess there’s the PVC type but couldn’t it have similar chemical issues and is it cost effective? 

http://contractormag.com/plumbing/cm_column_22/

http://www.chemaxx.com/polytube1.htm

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. RobWes | Apr 02, 2008 03:29am | #1

    PEX for too many reasons.

  2. User avater
    DDay | Apr 02, 2008 04:07am | #2

    Forget about the cost difference, if given a choice of pex or copper for the same price, I would always chose pex. I only would use copper in areas where you need the rigidity of copper like shower valves, heating pipes around the boiler, etc.

  3. plumbbill | Apr 02, 2008 04:23am | #3

    I'm an old school plumber that has mainly dealt with copper for water supply.

    First introduced to pex in 1990 for radiant heat applications.

    First introduced for potable systems was 2001 for me.

    I was leary about recomending it to anyone at first for potable systems.

    Other than it looking like crapp i haven't had any problems with Wirsbo brand.

    Your first link is standard for any potable water system------ it has to be sized correctly. Too many fittings is bad for any system no matter what the material is.

    His comment on compression style fittings is misleading, most compression style fittings have a stiffener insert for plastic piping.

    I have heard & read about MTBE being introduced into potable water from pex since 2006, I am doing more fact finding before I post my opinion wether pex is good for potable systems or not.

    I am a member of ASPE ( American Society of Plumbing Engineers) & am currently looking into pex leaching benzene as well MTBE.

    “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

  4. User avater
    xxPaulCPxx | Apr 02, 2008 04:24am | #4

    So what it comes down to, from the links is:

    1.>  Build it the way it is supposed to be built - OK, Duh!  I know this is news to some... but, DUH!

    2.>  Don't use pipe that is more than 7 years old.  I would be impressed if you could FIND 7 y.o. pipe anywhere besides a yard sale.  A store that has inventory on its shelf for 7 years is... out of business already!

    Rebuilding my home in Cypress, CA

    Also a CRX fanatic!

    If your hair looks funny, it's because God likes to scratch his nuts.  You nut, you.

    1. User avater
      rjw | Apr 02, 2008 07:55pm | #10

      >>So what it comes down to, from the links is:
      . . . .
      >>2.> Don't use pipe that is more than 7 years old. Seems to like an overly broad reading of the note regarding 2001 and changes since then.

      Remember Mary Dyer, a Christian Martyr (Thank you, Puritans) http://en.wikipedia.org/wiki/Mary_DyerMay your whole life become a response to the truth that you've always been loved, you are loved and you always will be loved" Rob Bell, Nooma, "Bullhorn"

      1. User avater
        xxPaulCPxx | Apr 03, 2008 06:08am | #11

        As the article didn't report that this was a problem with ALL pex pipe (was this PEX supposed to be used for Hydronic heat, not potable water?), AND since it said that "manufacturers are aware of this problem and may have made changes since 2001", AND it also says the contaminents wash out over time.

        It's like the local news, trying to be relavent by making you fear ordinary things in your home that are unlikely to do any harm, by reporting "A POTENTIAL DEADLY THREAT IN YOUR HOME - WHAT YOU CAN DO TO STAY SAFE - MORE AFTER THE BREAK"

        It sounds like they ae taking a known loaded sample and trying to extrapolate a wider danger.  They don't independently sample other commonly available tubing to see if this is industry wide, company wide, or even a batch problem.  MTBE contamination can be a BIG deal, if it was out there I think there would be a regular stink being made by the very people PEX hurts the most:  Union Plumbers

        I've yet to see a Union Plumber PSA warning about the dangers of PEX contamination.Rebuilding my home in Cypress, CA

        Also a CRX fanatic!

        If your hair looks funny, it's because God likes to scratch his nuts.  You nut, you.

        1. WindowsGuy | Apr 03, 2008 08:23pm | #18

          "MTBE contamination can be a BIG deal, if it was out there I think there would be a regular stink being made by the very people PEX hurts the most:  Union Plumbers"

          I'm curious.  Why are you are expecting Union plumbers to know about and be concerned by MTBE contamination?  They're not chemists after all.  Moreover, should contamination be found, plumbers in general would be the recipients of a whole lot of work replacing all the plastic pipe out there - PEX and CPVC.

          History has shown that the installation people in an industry using a product are generally the last to cry foul unless it hits their bottom line because of product failure.   Examples include:  Painters - High VOC solvent paints, HVAC engineers - freon, Siding - Asbestos, etc.  It's the manufacturers that typically know, deny, and hide when issues of safety arise.

          For my money, I will use copper and not worry about chemicals leaching into my water supply.  Copper would have to cost a pretty big multiple of PEX before I would even think of switching.  One man's opinion.

          1. User avater
            xxPaulCPxx | Apr 04, 2008 12:53am | #19

            I would expect them to trumpet it loudly if it could be used to make the case that copper should be used instead of PEX.  Copper is much more labor intesive then PEX, just like EMT is more labor intensive than Romex.

            As far as the price multiple, I see a 60' role of type L 1/2" copper at $2.60 a foot, while the last roll of PEX I bought (100') was $.36 a foot. 

            That's 4 times as expensive already, not including the extra labor of sweating each fitting.  Exactly how much more expensive does it have to be before you would consider using it?

             

             Rebuilding my home in Cypress, CA

            Also a CRX fanatic!

            If your hair looks funny, it's because God likes to scratch his nuts.  You nut, you.

          2. WindowsGuy | Apr 04, 2008 01:36am | #20

            A labor study done a couple of years ago actually found it was only 20% cheaper to run PEX than Copper. 

            http://www.toolbase.org/pdf/fieldevaluations/brighton_plumbingreporttask1.pdf 

            They used identical floor plans and crews and did multiple houses as a comparison.  Now, given the rise in Copper prices, I would expect the numbers to have changed, but the main savings are still probably not in the materials, but in the labor.

            Comparing raw material costs between PEX and Copper is misleading.  It's my understanding that most PEX installs do not run identical to Copper.  While branching and terminations using PEX can be done like Copper runs, most times manifolds and home runs are used greatly increasing the amount of PEX used vs Copper.

            How much of a cost differential would push me to PEX?  Hard to say. 

            Would I buy a car today without crumple zones, fuel tank protection, or airbags just because it was cheaper?  No.  Would I use undersized lumber in a structural application just because it was cheaper?  No.  Would I install inadequate gauged wiring in a house just because it was cheaper?  No.  I see the safety concerns with PEX in much the same light even if my comparisons are not perfect.

            I'm not installing something behind a wall that I even suspect might cause me harm down the road.  Why risk it if you can afford not to? 

            Edited 4/3/2008 6:37 pm ET by WindowsGuy

          3. frammer52 | Apr 04, 2008 03:32am | #21

            My understanding is that pex has been in use in europe for 50 years.

            Now window guy, don't you think it would have been off the market

            a long time ago.

            as far as comparrisons between them,  they probably used the same plumbers.

            By doing this they skewed the results.  How you might ask, well the

            plumbers in america have very limited experience with pex.  I know that

            plumbers in america have been sweating pipes for years.  As far as

            price, the pex is getting cheaper everyday when comparring materisl costs, because copper is going up and up.

            The advantages of pex is the home runs back to the manifold.  Less

            reduction inh2o preasure.

          4. plumbbill | Apr 04, 2008 04:53am | #22

            My understanding is that pex has been in use in europe for 50 years.

            Not exactly, pex as we know it was invented in about 68, Engal & Silane methods.

            Didn't hit the market until the 70's, & that was for radiant heat applications.

            Late 70's for Europe to use as domestic water. 84 when the product hit the US.

            I'm not sure who allowed it first in the US for domestic water, but upc was the 2000 code adopted in 01.

            Now window guy, don't you think it would have been off the market

            a long time ago.

            How long was asbestos on the market?

            plumbers in america have very limited experience with pex

            True, but let's not paint with such a broad brush. I have more experience with copper, but I have installed  9 miles of 1/2" pex since 2002.

            Depending on the design time savings will vary.

            The price differential in material with someone posting 60' type "L" soft is misleading.

            Average home is plumbed in type "M" rigid which runs about 50% of the cost of type "L" soft.

            The advantages of pex is the home runs back to the manifold.  Less

            reduction inh2o preasure.

            Actually not, the piping material does not affect the pressure.

            “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

          5. frammer52 | Apr 04, 2008 05:36am | #23

            I will bow to your knowledge.

            Do you still use copper, caste iron for waste?

          6. plumbbill | Apr 04, 2008 06:53am | #24

            Copper for the hot water mains.

            Stainless steel for the cold water mains.

            Uponor (pex) from the metered manifolds to each fixture.

            Cast iron for the main stacks & plenums.

            ABS for the branch dwv lines.

            Current job has ABS going through the floor due to the particular fire rated sleeve that we are using------ in theory the fire ring is supposed to be able to pinch off the abs if there is a fire.

            “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

          7. frammer52 | Apr 04, 2008 04:43pm | #25

            The reason I asked is, the plumbers around here had a hard time switching from cast to PVC.

            In fact in state law, commercial buildings in NY have to still use cast.

            We used to joke about plumbers full employment codes.

            Every time there is a new product, there is a natural resistance to

            try anything new.

            As far as Pex, I believe that there seems to be resistance by our

            local plumbers to use it.

            Personally I would never do any plumbing, rather have someone else

            do it.  I know my limitations.

          8. User avater
            talkingdog | Apr 04, 2008 05:41pm | #26

            I've seen some thin walled stainless products.
            Look and install similar to PEX, a bit more
            expensive, but all stainless. That's the
            way to go.

          9. plumbbill | Apr 05, 2008 02:18am | #28

            Our stainless is bige bore------ 2 to 6 inches.

            We can't run the hot water in it yet. I haven't received an actual scientific answer as to why yet.

            “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

          10. User avater
            talkingdog | Apr 05, 2008 05:24pm | #30

            We have stainless that looks just like ordinary galvanized pipe.
            Whole selection at my local hardware store. A bit more expensive
            though.I think the thinwall stuff is really cool.

            Edited 4/5/2008 10:24 am by talkingdog

          11. WindowsGuy | Apr 04, 2008 07:23pm | #27

            Plumbbill gave some good facts.

            In general, I never believe in a product (or person for that matter) based solely on the "years in service" argument.  Way too many examples of bad things coming to light years after a product is in service.

            PEX and CPVC are petroleum-based.  I will admit to a growing anti-petroleum bias.  (yes I know copper production is no environmental angel either)

            As for Cast Iron, wouldn't you know it, high end homes specify it to cut down on noise.  Every time a toilet flushes on an upper floor in my house, I wish I had cast iron.  Of course, having dealt with some CI in a 100 year old house I used to own, I know that PVC is clearly easier to handle.

  5. User avater
    BillHartmann | Apr 02, 2008 05:00am | #5

    The first one is not a problem is PEX. It is a problem with some one that had absolutely no concept of flow rates, pressure drops and sizing.

    What the article says is that PEX still follows the laws of physics. And while it is easier to install you still need an IQ higher than a toad.

    Like wise the 2nd article indicates that the problem is only with certain methods of processing and even at that it can easily be flushed.

    Used irridated PEX.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
  6. MikeHennessy | Apr 02, 2008 02:56pm | #6

    If you look at the articles, the first one appears to slam PEX, but the analysis shows that the culprit was undersized piping, not the material the pipes were made of. You just need to account for the distance & fittings and you're good.

    The second article does not condemn all PEX -- it specifically notes that certain brands release chems, but that others don't. It also states that the tested material was all manufactured pre-2001, and that mfgrs have since changed the makeup of the product.

    In my book, you have 2 choices, and only 2 choices, for supply lines -- copper or PEX. Price them out, and let your customer decide. (If he wants to feed his research/engineering jones, let him research which brands of PEX are chem-free and let him size the lines. It'll keep him busy.)

    Mike Hennessy
    Pittsburgh, PA

    1. GPAH | Apr 02, 2008 06:37pm | #9

      The first article referenced from Contractor Mag simply points out that this particular type of piping is and can be great - if the installer does their job correctly. PEX is not a silver-bullet that somehow gets an exception to the principals of hydraulics.

      No stiffeners are required with the insert fittings - the fitting is the stiffener. Annealed copper crimp rings, stainless steel clamps or PEX rings capture & hold the pex onto the somewhat-barbed insert fitting type described in the first link.

  7. frenchy | Apr 02, 2008 04:53pm | #7

    dogfish,

      At one time I started to replace all the CVPC and replace it with Copper.   Then came the articles about lead leaching so I switch to a low lead solder, I'm still not satisfied so for right now I'm reusing all of my old CVPC while I'm installing the pex for in floor radiant. 

     The detractors of CVPC are many and varied..

      The detractors of Copper are many and varied..

     The detractors of Pex can join in as well. 

     what's your favorite paint color? <grin>

    1. frammer52 | Apr 02, 2008 05:58pm | #8

      frenchy: you said it well. 

    2. plumbbill | Apr 03, 2008 08:39am | #12

      I switch to a low lead solder,

      What year are you talking about "low lead solder"?

      “The world is a dangerous place, not because of those who do evil, but because of those who look on and do nothing.” —Albert Einstein

      1. DougU | Apr 03, 2008 01:55pm | #14

        What year are you talking about "low lead solder"?

        Must have been when he was a little boy!

      2. User avater
        talkingdog | Apr 03, 2008 02:36pm | #15

        I recently found out that brass fittings are a health
        concern due to the lead content. WHO has issued a directive
        on this. Lead is added to brass formulations to improve
        machinability.AFAIK, there is only one company in the world that
        has commercialized a lead-free brass for use in plumbing,
        and that stuff, Eco-Brass, is not yet on the market.

        Edited 4/3/2008 7:38 am by talkingdog

        1. JimB | Apr 05, 2008 03:28am | #29

          Brass plumbing fittings can contain upto about 10% lead.  However, the chemistry of the water in the system affects how much lead is leached from the fittings.  Hard water helps prevent leaching because the minerals deposited on the fittings protect the brass from the water.  Acidic water tends to increase leaching. 

          I'm surprised that the second article in the OP didn't mention anything about the chemistry of the water in the systems where the MTBE was found.  I'd find it hard to believe that water chemistry doesn't factor in to leaching of chemical from PEX.

      3. jayzog | Apr 03, 2008 02:38pm | #16

        I built my own house in 1986, plumbed everything with 50-50. Got the water tested in 95 when my wife was expecting, lead was to little to detect.

        Hardly scientific, but hardly a worry either.

    3. User avater
      bill_mcgonigle | Apr 03, 2008 09:00am | #13

      Besides the solder I read recently that many brass fittings contain lead. Like probably all those full-port ball valves I put in... blame my spelling errors on them.

  8. User avater
    bp21901 | Apr 03, 2008 07:35pm | #17

    Here is something I came across recently dealing with a specific company's brass fittings for PEX. The only date I noticed was 2003 so I don't know if it is resolved yet or not.

    http://www.zurnclassaction.com/index.html

  9. ac_dc | Apr 04, 2011 10:54am | #31

    PEX in cement?

    We are replacing Cu water supply lines which are currently in the slab.  I have a 2" deep x 4" wide x 30' long trench prepared in the slap and plan to run PEX to the bathroom.  Is it okay to use foam insulation around the PEX and then cover everything with fresh cement?  Is there a better approach?  Thanks!

    1. Scott | Apr 04, 2011 03:14pm | #33

      I think so. Just be sure to

      I think it will be OK. Just be sure to pressure test it before you pour.

  10. sawzall316 | Apr 04, 2011 02:32pm | #32

    Your customer needs to focus

    Dispite the nay sayers, Pex is and will be the material of choice for the forseeable future accross the country bar none with the exception of both the Chicago and New York metro areas. Properly designed and installed, a Pex installation out performs copper hands down, why on God's green earth is this even an issue! When one factors labor, again, there is no contest.

    With the exeption of rodents eating through Pex---which is something I never thought of and quite franky didn't know was an issue, Pex has the same general vulnerabilitie as copper in that is easy to puncture. However, when freezing conditions are factored in, again, copper is no match for Pex.

    The upside of Pex is overwelming, however, if your customer plans on suckling the faucet 24-7 then yes he may have an issue late in his life relative to leeching.

    1. [email protected] | Apr 05, 2011 03:09pm | #34

      With acidic waters, copper leaching can be a problem.

      Depending on the acidity of the water, copper can leach enough to be a health concern. 

      Sure some brands of pex might have had problems with leaching.   But, I'd still be more comfortable with pex, than copper for a lot of reasons. 

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Summit 2025 — Design, Build, Business

Join some of the most experienced and recognized building professionals for two days of presentations, panel discussions, networking, and more.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Grout-Free Shower Panels
  • Prep Faster With Peel-and-Stick
  • One-System Wonder
  • Versatile Vise

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data